Thread: Ventilation specs for darkroom

  1. #21
    Tin Can's Avatar
    Join Date
    Dec 2011
    Posts
    22,454

    Re: Ventilation specs for darkroom

    Quote Originally Posted by RodinalDuchamp View Post
    For anyone interested:
    So you will need a low volume fan, perhaps a computer fan will work


    (4) There should be at least 10 air changes per hour in the room to ensure removal of
    chemical fumes from the area. The supply should be located so that it does not “short
    circuit” and feed directly to the exhaust. A darkroom supply of 50% of the exhaust
    rate is ideal.
    Tin Can

  2. #22

    Join Date
    Jul 2016
    Posts
    4,566

    Re: Ventilation specs for darkroom

    Quote Originally Posted by RodinalDuchamp View Post
    (4) There should be at least 10 air changes per hour in the room to ensure removal of
    chemical fumes from the area.
    Beyond norms, the key is not to have turbulence. Air has to flow laminar from the emision sources to the extraction, in that way fumes are never breathed. If we have turbulence we always breath some fumes, and we need a lot of air changes to keep fumes concentration low, but it will never be zero. With a properly designed system we breath zero fumes.

    A properly designed system is essential when we use some kind of chem.

  3. #23
    Tin Can's Avatar
    Join Date
    Dec 2011
    Posts
    22,454

    Re: Ventilation specs for darkroom

    I am out as Pere and Drew tango

    Make up air is important and can be very cold or hot depending on location, climate
    Tin Can

  4. #24

  5. #25
    Drew Wiley
    Join Date
    Sep 2008
    Location
    SF Bay area, CA
    Posts
    18,377

    Re: Ventilation specs for darkroom

    A computer fan????? That's like a mouse dueling a mountain lion. Wrong Holiday. This is Halloween, not April Fools Day.

  6. #26
    adelorenzo's Avatar
    Join Date
    Dec 2012
    Location
    Whitehorse, Yukon
    Posts
    457

    Re: Ventilation specs for darkroom

    I was reading Tim Rudman's toning book last night and he also recommends a minimum of 10 ACH.

  7. #27
    Tin Can's Avatar
    Join Date
    Dec 2011
    Posts
    22,454

    Re: Ventilation specs for darkroom

    OP is trying to figure out DR ventilation for a 6 X 6 X 7ft shed. 252 cubic feet

    He needs a small fan, 240 CFM is too big by a factor of 10

    Quote Originally Posted by adelorenzo View Post
    I was reading Tim Rudman's toning book last night and he also recommends a minimum of 10 ACH.
    Tin Can

  8. #28
    adelorenzo's Avatar
    Join Date
    Dec 2012
    Location
    Whitehorse, Yukon
    Posts
    457

    Re: Ventilation specs for darkroom

    Quote Originally Posted by Tin Can View Post
    OP is trying to figure out DR ventilation for a 6 X 6 X 7ft shed. 252 cubic feet

    He needs a small fan, 240 CFM is too big by a factor of 10
    I wasn't making any comment on the size of the fan required, I was just giving the OP another data point for recommended air changes per hour.

  9. #29
    Tin Can's Avatar
    Join Date
    Dec 2011
    Posts
    22,454

    Re: Ventilation specs for darkroom

    I know you were. I was trying to repeat his needs

    All good

    Quote Originally Posted by adelorenzo View Post
    I wasn't making any comment on the size of the fan required, I was just giving the OP another data point for recommended air changes per hour.
    Tin Can

  10. #30
    Drew Wiley
    Join Date
    Sep 2008
    Location
    SF Bay area, CA
    Posts
    18,377

    Re: Ventilation specs for darkroom

    You don't know what you're talking about, Tin Man, or I am confusing you with a character in Wizard of Oz? If you take 240CFM, factor in hydrostatic pressure outside on a rainy day, or even in a humid climate, and then air friction from ductwork that cannot be straight because it has to prevent light entering and may very well be corrugated for ease of installation, the real world capacity is about half that air volume at best. Then one always needs a boost factor, even if ordinarily running it at lower volume, in case there's a spill of something you want rapidly exhausted, or during mixing of some concentrated chemical. So a fan of at least 180 cfm is called for, or even better, 240 because there's such an excellent in-line option in that case. That would be the routine specification for even a bathroom that size, where mainly just water vapor is involved, unless the climate is routinely arid. What one doesn't want is a cheap ceiling-mount propeller-style fan that is as noisy as a gas lawn mower.

Similar Threads

  1. Darkroom ventilation fan
    By BetterSense in forum Darkroom: Equipment
    Replies: 15
    Last Post: 7-Apr-2011, 18:57
  2. Darkroom ventilation problem?
    By jamespayne in forum Darkroom: Film, Processing & Printing
    Replies: 4
    Last Post: 27-Apr-2010, 22:13
  3. Garage Darkroom Ventilation
    By Matthew Cordery in forum Darkroom: Film, Processing & Printing
    Replies: 7
    Last Post: 15-Aug-2004, 19:56
  4. Bad ventilation in darkroom
    By Yaakov Asher Sinclair in forum Darkroom: Film, Processing & Printing
    Replies: 24
    Last Post: 25-Jun-2002, 10:19
  5. darkroom ventilation
    By Raven Garrow in forum Darkroom: Film, Processing & Printing
    Replies: 9
    Last Post: 23-Jul-2000, 21:43

Bookmarks

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •